Re: Cheater Cord (was: Run 2 roof A/C on 30 Amp?)

Staging area for content imported from the old Yahoo group. This forum is LOCKED. Moderators may edit content and relocate to other forums as appropriate.
mel96safari
Posts: 719
Joined: Thu Mar 19, 2015 7:06 am

Run 2 roof A/C on 30 Amp?

Post by mel96safari »

'
Need to run 2 A/Cs on 30 amp service? It's supposed be possible with 2 of these $299.00 devices 


https://www.rvupgradestore.com/Micro-Air-ASY-364-X20-IP-EasyStart-364-AC-p/asy-364-x20-ip.htm

Important Note: Each AC unit requires an EasyStart unit to be installed.

Mel'96 Sahara


'
TD
Posts: 767
Joined: Fri May 16, 2014 4:01 am

Re: Run 2 roof A/C on 30 Amp?

Post by TD »

'Mel,
Thank you for the info. These units are probably very handy, especially if one is trying to run an a/c unit on a small generator.Just an fyi, I have never had an issue running both a/c units on 30amp power, but it does require switching the refrigerator to propane and not using any other heavy loads. I have done this many time on my Safari and also on my last unit, a Holiday Rambler. If one needs to use a high draw item like a microwave, then one a/c unit needs to be shut down until the microwave is no longer needed.


John
'95 Safari Serengeti 38ft, 300 Cummins 8.3CTA, Allison
6spd.
On Sun, Feb 17, 2019 at 12:55 PM stuplich@... [Safarifriends] wrote:



Need to run 2 A/Cs on 30 amp service? It's supposed be possible with 2 of these $299.00 devices 


https://www.rvupgradestore.com/Micro-Air-ASY-364-X20-IP-EasyStart-364-AC-p/asy-364-x20-ip.htm

Important Note: Each AC unit requires an EasyStart unit to be installed.

Mel'96 Sahara



'
Eddie Windom
Posts: 3
Joined: Fri Jan 18, 2019 12:00 am

Re: Run 2 roof A/C on 30 Amp?

Post by Eddie Windom »

'ImageLeisureCords 24'' RV Y Adapter Cord 50Amp Female Plug to One 30 Amp Male...Splits your 50 Amp Female to 30 Amp Male or 15 Amp Male -Specifications100% copper wire conductor inside -Heavy-...


Eddie2000 Safari Continental
On Sunday, February 17, 2019, 12:55:54 PM EST, stuplich@... [Safarifriends] wrote:


 

Need to run 2 A/Cs on 30 amp service? It's supposed be possible with 2 of these $299.00 devices 


https://www.rvupgradestore.com/Micro-Air-ASY-364-X20-IP-EasyStart-364-AC-p/asy-364-x20-ip.htm

Important Note: Each AC unit requires an EasyStart unit to be installed.

Mel'96 Sahara


'
Gerald Emert
Posts: 8
Joined: Wed Jan 11, 2017 12:54 am

Re: Run 2 roof A/C on 30 Amp?

Post by Gerald Emert »

' I have one of these but have been unable to use it.  Every time I try it pops the breaker on the pedestal.  I believe I've heard that it won't work with GFCI outlets.  Was a waste of money for me so far. Jerry 03 Beaver PT From: Safarifriends@yahoogroups.com on behalf of Eddie Windom edbo_n_go@... [Safarifriends]
Sent: Monday, February 18, 2019 01:12
To: Safarifriends@yahoogroups.com
Subject: Re: [Safarifriends] Run 2 roof A/C on 30 Amp?
   
If there is a 15/20 amp plug in addition to the 30 Amp, you might consider getting one of these to bring you up to what you need:  LeisureCords 24'' RV Y Adapter Cord 50Amp Female Plug to One 30 Amp Male and One 15 Amp Male 2.5 Feet with Handle (50 Amp Female - (1) 30 Amp Male & (1) 15 Amp Male)
$29.99 Image LeisureCords 24'' RV Y Adapter Cord 50Amp Female Plug to One 30 Amp Male... Splits your 50 Amp Female to 30 Amp Male or 15 Amp Male -Specifications100% copper wire conductor inside -Heavy-...


Eddie 2000 Safari Continental
On Sunday, February 17, 2019, 12:55:54 PM EST, stuplich@... [Safarifriends] wrote:

 

Need to run 2 A/Cs on 30 amp service? It's supposed be possible with 2 of these $299.00 devices 


https://www.rvupgradestore.com/Micro-Air-ASY-364-X20-IP-EasyStart-364-AC-p/asy-364-x20-ip.htm

Important Note: Each AC unit requires an EasyStart unit to be installed.

Mel '96 Sahara


'
mel96safari
Posts: 719
Joined: Thu Mar 19, 2015 7:06 am

Cheater Cord (was: Run 2 roof A/C on 30 Amp?)

Post by mel96safari »

'Before you waste $30+ be aware that those "cheater cords" are useless if/when the 15/20 Amp pedestal receptacle is GFCI protected, (which most are).
Mel'96 Sahara


---In Safarifriends@yahoogroups.com, wrote :

ImageLeisureCords 24'' RV Y Adapter Cord 50Amp Female Plug to One 30 Amp Male...Splits your 50 Amp Female to 30 Amp Male or 15 Amp Male -Specifications100% copper wire conductor inside -Heavy-...


Eddie2000 Safari Continental

'
Craig Burrell
Posts: 66
Joined: Fri Jun 30, 2017 6:42 am

Re: Cheater Cord (was: Run 2 roof A/C on 30 Amp?)

Post by Craig Burrell »

' that sounds like experience speaking. How did you find that out?
On Monday, February 18, 2019, 11:13:08 AM CST, stuplich@... [Safarifriends] wrote:


 
Before you waste $30+ be aware that those "cheater cords" are useless if/when the 15/20 Amp pedestal receptacle is GFCI protected, (which most are).
Mel'96 Sahara


---In Safarifriends@yahoogroups.com, wrote :

If there is a 15/20 amp plug in addition to the 30 Amp, you might consider getting one of these to bring you up to what you need:  LeisureCords 24'' RV Y Adapter Cord 50Amp Female Plug to One 30 Amp Male and One 15 Amp Male 2.5 Feet with Handle (50 Amp Female - (1) 30 Amp Male & (1) 15 Amp Male)
$29.99
ImageLeisureCords 24'' RV Y Adapter Cord 50Amp Female Plug to One 30 Amp Male...Splits your 50 Amp Female to 30 Amp Male or 15 Amp Male -Specifications100% copper wire conductor inside -Heavy-...



Eddie2000 Safari Continental

'
mel96safari
Posts: 719
Joined: Thu Mar 19, 2015 7:06 am

Re: Cheater Cord (was: Run 2 roof A/C on 30 Amp?)

Post by mel96safari »

'Experiance
Image Mel'96 Sahara

---In Safarifriends@yahoogroups.com, wrote :

that sounds like experience speaking. How did you find that out?
'
drralph111
Posts: 2
Joined: Wed Mar 06, 2019 7:18 am

Re: Cheater Cord (was: Run 2 roof A/C on 30 Amp?)

Post by drralph111 »

'Can you use this with two 30 amp outlets using a 30 amp to 20 amp adapter for the second one.  I know that it would bring the total up to 60 but is that acceptable?


Sent from my Verizon, Samsung Galaxy Tablet
-------- Original message --------From: "Craig Burrell technolog1@... [Safarifriends]" Date: 2/19/19 8:08 AM (GMT-05:00) To: "stuplich@... [Safarifriends]" Subject: Re: [Safarifriends] Cheater Cord (was: Run 2 roof A/C on 30 Amp?)
 
that sounds like experience speaking. How did you find that out?
On Monday, February 18, 2019, 11:13:08 AM CST, stuplich@... [Safarifriends] wrote:


 
Before you waste $30+ be aware that those "cheater cords" are useless if/when the 15/20 Amp pedestal receptacle is GFCI protected, (which most are).
Mel'96 Sahara


---In Safarifriends@yahoogroups.com, wrote :

If there is a 15/20 amp plug in addition to the 30 Amp, you might consider getting one of these to bring you up to what you need:  LeisureCords 24'' RV Y Adapter Cord 50Amp Female Plug to One 30 Amp Male and One 15 Amp Male 2.5 Feet with Handle (50 Amp Female - (1) 30 Amp Male & (1) 15 Amp Male)
$29.99
ImageLeisureCords 24'' RV Y Adapter Cord 50Amp Female Plug to One 30 Amp Male...Splits your 50 Amp Female to 30 Amp Male or 15 Amp Male -Specifications100% copper wire conductor inside -Heavy-...



Eddie2000 Safari Continental


'
wolfe102001
Posts: 502
Joined: Sun Feb 17, 2013 6:23 am

Re: Cheater Cord (was: Run 2 roof A/C on 30 Amp?)

Post by wolfe102001 »

'Would it work-- yes.
BUT, only because 30 amp has no GFI protection.
And, if the two hots are on the same side/phase, you could overload the neutral.  In a properly wired 50 amp circuit, the neutral only carries the DIFFERENCE in loads between L1 and L2.  In your example, the neutral could carry the SUM of loads on L1 and L2.
'
Dale Maggio
Posts: 470
Joined: Sat Jan 21, 2012 3:23 am

Re: Cheater Cord (was: Run 2 roof A/C on 30 Amp?)

Post by Dale Maggio »

'I was going to suggest a stick of dynamite in the electrical bay would accomplish the same thing.  I seriously doubt they would know how or where to check phasing.
-=Dale=-
On ?Wednesday?, ?March? ?06?, ?2019? ?06?:?41?:?30? ?PM? ?PST, bawolfe10@... [Safarifriends] wrote:


 
Would it work-- yes.
BUT, only because 30 amp has no GFI protection.
And, if the two hots are on the same side/phase, you could overload the neutral.  In a properly wired 50 amp circuit, the neutral only carries the DIFFERENCE in loads between L1 and L2.  In your example, the neutral could carry the SUM of loads on L1 and L2.
'